Quote:
Originally Posted by OneMoBear
The "load" seems pretty obvious but will we connect the feed for the TM AND the inverter there? It seems we would want both the TM and the inverter tied in past our cutoff switch. So, we could go from the hot side of the "load" to the feed for the cutoff and then to the TM and inverter from there. Then grab the negative side for the TM at "load" and the inverter at either the battery or on the "load" on the controller. I know I must be driving all the engineers here crazy with my goofy descriptions . . .
Malinda
|
What you have described will work but may not be the best way.
First:
what is the maximum current the controller "load" will handle? It may not be enough for your inverter + refrig on DC + heater fan + Water pump + recirc pump on the toilet + lights etc.
Your current wiring is most likely battery to the converter, That will be your TM load.
Second:
The inverter wiring needs to as short as possible between the battery and inverter. The inverter is going to use the most "watts" followed by the refer on DC.
IMO you should separate some on these items out.
The little I have looked at the controllers with "load" outputs, the intent is to disconnect "load" from the battery when it drops below some voltage set point.
This is done to allow the solar panels to recharge the battery(ies).
Most people put a battery disconnect switch in to remove all load from the battery. Since you may want to charge the battery with the TM closed from the solar panels I would put the switch between the fuse at the battery and all load. Wire the controller output + at the fuse to disconnect switch connection.