Originally Posted by Casey Freswick View Post
I have finished wiring my new solar system. Everything is working great. Here is a picture of my completed panel.
I would recommend NOT putting multiple wires on a singe connector. This is especially true on the inverter. You might want to have a dedicated ground busbar and a dedicated positive busbar. Have a single 2/0 wire going from the battery pos to the pos busbar and a single 2/0 wire from the battery to the neg busbar. Then run a single 2/0 cable from each busbar to your inverter. Run all of your ground wires (singly) to an empty port on the ground busbar and the same with the positive busbar.

The optimum system will have only 1 wire on any singe terminal with the odd exception of 2 (smaller) wires on one terminal. What you have going on, on your inverter may cause you problems down the road. You will certainly have a lack of continuity and an increase of heat and corrosion.

You might want to try to find busbars (sometimes called "Distribution Blocks") like these. Be sure they are rated 250A.

https://www.amazon.com/Hoteam-Distri...%2C185&sr=8-18